Your element will draw about 23A at full power, so a 25A breaker should be sufficient. It's possible that the breaker is tripping at lower than rated amps (i.e. bad.) You could replace with a 32A breaker, as long as the wires are 10AWG or heavier. You can get a 2 pole 32A, DIN rail, UL rated breaker much cheaper here.
It looks like that breaker only carries the element current in your control box. Is this correct? The reason I asked about a volt/ohm meter, is that it is possible that your element is bad, and thus drawing too much current, causing the breaker to trip. Measureing the resistance between all three pairs of prongs on the plug can tell you if the element is the problem. The resistance between the two hot prongs should be ~10.47 ohms, and the resistance between either of the hot prongs and the ground prong should be infinite (on the highest resistance range of the meter.) If any of these resistances are less than this, then the problem is either in the element, the cord, or the plug.